The messages from the EZIO8SA Inputs are Scene/Group messages. Insteon allows only one Scene/Group to run at a time, cancelling one Scene in favor of the next. Not unique to the EZIO8SA. If it was possible to press the paddle of two SwitchLincs at the same exact instant only one would report. Not sure if that is the problem as I did not follow the explanation of multiplexing.

Suggest changing each Input one at a time to verify that each Input is reporting state changes to the ISY. The ISY only understands digital mode so if the analog inputs are set up for analog mode the Alarm settings need to be established. If the analog inputs are not used they need to be connected to EZIO8SA Gnd so they do not float. The analog inputs have no built in pullup resisters so they will generate false state change messages if not locked to Gnd.

The Utility trace has to be posted as simple text. The Insteon commands specific to the EZIOxx family of devices can be found in the Download section. Not sure you will find much detail about PLM message formats as SmartLabs considers that information confidential. You can get a Developer Subscription but that requires an NDA be signed which precludes sharing of the information publicly.

In general the 0262 is the beginning of an outbound message.
16B0CC is the Insteon address of the device to receive the command
03 are flags and hop counts
28 is cmd1
00 is cmd2

1 :8 0262 16B0CC 032800

The PLM echoes each command which is the following message with the 06 appended.

1 :9 0262 16B0CC 032800 06

0250 in an inbound response to the command issued
16B0CC is the Insteon address of the device
13AC99 is the Insteon address of the PLM
2B are flags and hop counts
28 is cmd1
00 is cmd2

1 :11 0250 16B0CC 13AC99 2B2800