Glad to hear you are working. The Input group number is used to search the link database looking for a “controller of” link record with a matching group number. A “controller of” link record with a matching group number provides the responder device Insteon address needed in the Group Cleanup Direct message. Without a match of group numbers, the 2X4 does not have the responder address needed to issue a Group Cleanup Direct message. Without at least one matching link record, the starting Group Broadcast message is also not sent.