Using the SHN 1.6 Utility, “Read” Settings for Insteon All_Link Group Commands function, the Group number from 0x40 (Input 1 Group number) is 0xFF. The SHN Utility displays a 25 (displays only 2 digits) for the Group value but the trace shows a 0xFF being returned from location 0x40. Using the “Write” function I changed the group number for Input 1 to 0x01 and confirmed that 0x40 was changed to 0x01 by doing a subsequent “Read”. Unfortunately the yellow “Save Changes” button caused the value of location 0x40 to be changed back to 0xFF. Changed the Group number for Input 1 back to 0x01 with a “Write” (confirmed with a subsequent “Read”) and tried to link Keypadlink button 5 to the 2X4 (without doing a “Save Changes”). Same situation, continuous 13 commands with group number 0xFF issued to the Keypadlinc device and a “Read” of Input 1 information shows the Group number for Input 1 has been changed back to a 0xFF. Something in the linking process must have changed the group number for Input 1 back to 0xFF. Turning off the 2X4 is the only way to stop the flow of 13 commands from the 2X4. When power is returned to the 2X4, the command 13 sequence picks up again. Only way I have found to stop the flow of commands from the 2X4 is to do a factory reset on power up of 2X4. Various combinatiions using the Set button has no affect in stopping the command flow from the 2X4. Sure hope someone has an idea of where to go from here.