@asw24b wrote:

I have a set up where I am trying to only use 1 output port of the 2×4; I don’t need to read the inputs.

Unfortunately, I get a constant stream of input status changed messages for I3 and I4.

Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 0, 1
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 0, 0
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 1, 0
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 1, 1
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 0, 1
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 0, 0
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 1, 0
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 1, 1
Received INSTEON “IO2x4 in Hall Closet” inputs status changed: 0, 0, 0, 1

I tried connecting I3 and I4 to GND, but it still happens… is there some relevant info missing from the quick start guide ?

Thanks.
Mike

I get the same symptom. Tying I3 and I4 to ground does not prevent the inputs from cycling on/off and sending status change announcements. However, if I connect the inputs to +5V with a pullup resistor, the inputs stay on and the status broadcasts stop. Do I have a defective unit or am I missing something?